[APP][Pro] Uponor Smatrix
Hello community,
In my quest to migrate completely from Home Assistant to Homey Pro, I have created an app for my Uponor underfloor heating system.
It currently only supports the Uponor Smatrix Pulse system as I have that system at home to test with, but it might also work with Smatrix Wave (if they share the same custom application protocol).
Features
  • Works fully locally (LAN), no Internet / cloud connection needed
  • Auto-discovery based on the MAC manufacturer prefix of Uponor
  • Enter an IP address manually if for some reason auto-discovery does not work in your network
  • Each room thermostat is added as an individual device, so you get room-level insight and control
  • Automatically gets the user-configured name of each thermostat (from the Uponor app), so user-friendly device names out of the box
  • Currently supports reading the temperature (every minute) and setting the target temperature (setpoint)
Coming soon
  • Support for thermostat mode control (auto/heating/cooling/off)
  • Support for other thermostat and controller models (depending on community testing)
Eye candy
Some screenshots to convince you that this is a legit app :sweat_smile:
Source code
Of course the code for this app is open source and available on GitHub.
Enjoy and let me know if this app helps you manage your Uponor system!
Nice I was hoping for this. But for me it doesn’t work. I suppose smatrix pulse isn’t the same thing?
Nvm works fine!
The app works fine mostly. But I have two issues, which we can hopefully easily fix.
  1. Some of my rooms have the “Could not connect to Uponor controller on IP address 10.0.1.249” error. Although not all of them and its all the same controller. I have about 8 rooms which a uponor wall unit thing. So maybe we can do something with a higher timeout? or?
  2. I get slightly different reading compared to their app. Thing like: room temperature is set to 20.1c while the app says 20c. Not a biggy.
Hi!
  1. Usually it works to restart the Uponor app from the Homey settings. I’m working on an update that tries to reconnect automatically. This is mainly caused by the Uponor communication module being quite unstable. You can also try to override the IP address in the device settings so that it doesn’t rely on network discovery.
  2. Homey only allows the temperature property to be set with increments of 0.5 degrees (to fit the UI elements for thermostat control). So unfortunately I cannot show the temperature more fine-grained than this.
Great to have the Uponor Smatrix app available on Homey Pro, I have been looking for this for a while :grin:
Here are some initial feedbacks:
  • When I try to change the temperature set point from the app when the “Eco” mode is active, I seem to get wrong temperature set point in Uponor system app? Seems like it is not compensating for the “Eco” set point?
  • Would also be great if you could include “humidity” and “battery” status in the app😉
Hi, thanks for using the app and your feedback!
I’ll have a look into Eco mode. I never use it personally (because underfloor heating works best when kept at a stable temperature in my experience). There are separate API properties for Eco mode settings, so I would have assumed that the Uponor controller calculates this offset by itself.
I personally don’t have humidity and battery data (I’m using a wired system, and I don’t have humidity sensors in the thermostats), so in order to implement this, I would need a copy of the API data you’re receiving (you can find debug data in the device settings, simply enable it and copy the contents here or in a private message).
Chris
Hi
First I have to thank you for making this app. finally :slight_smile:
I don’t know if you have received a reply to the post above.
Here are the error codes I get from one of mine thermostats
DEL 1
{"result":"OK","output":{"vars":[{"waspVarName":"cust_New_ControllerSW","waspVarValue":"0"},{"waspVarName":"cust_CX_SW_Distributed","waspVarValue":"0"},{"waspVarName":"cust_Start_SW_Update","waspVarValue":"0"},{"waspVarName":"cust_Update_Counter_TimeOut","waspVarValue":"0"},{"waspVarName":"cust_Update_SW_Retries","waspVarValue":"0"},{"waspVarName":"cust_SW_Update_Fail","waspVarValue":"0"},{"waspVarName":"cust_Mini_FW_Updated","waspVarValue":"0"},{"waspVarName":"cust_General_RH_Setpoint","waspVarValue":"75"},{"waspVarName":"cust_controller_1_lost","waspVarValue":"0"},{"waspVarName":"cust_SW_version_update","waspVarValue":"X265_117.hex"},{"waspVarName":"cust_Controller1_Name","waspVarValue":"Uponor sentral"},{"waspVarName":"cust_C1_T1_name","waspVarValue":"Bad Vaskerom"},{"waspVarName":"cust_C1_T2_name","waspVarValue":"Stue"},{"waspVarName":"cust_C1_T5_name","waspVarValue":"Soverom MBR"},{"waspVarName":"cust_C1_T6_name","waspVarValue":"Bad MBR"},{"waspVarName":"cust_C1_T7_name","waspVarValue":"Soverom Alina"},{"waspVarName":"cust_C1_T8_name","waspVarValue":"Soverom Fine"},{"waspVarName":"cust_C1_T9_name","waspVarValue":"TV-Stue"},{"waspVarName":"cust_C1_T10_name","waspVarValue":"Entre"},{"waspVarName":"cust_C1_T11_name","waspVarValue":"Soverom Leah"},{"waspVarName":"cust_wifi_device","waspVarValue":"Nett"},{"waspVarName":"cust_ip_device","waspVarValue":"192.168.147.185"},{"waspVarName":"cust_Enable_SW_Update","waspVarValue":"1"},{"waspVarName":"cust_Succesfull_SW_Instal","waspVarValue":"0"},{"waspVarName":"cust_Temporary_ECO_Activation","waspVarValue":"1"},{"waspVarName":"cust_myecoprofile_name_1","waspVarValue":"Test ECO profil Soverom MBR"},{"waspVarName":"cust_C1_T5_Custom_Eco_Profile","waspVarValue":"0"},{"waspVarName":"cust_Low_temperature_Limit","waspVarValue":"590"},{"waspVarName":"cust_Enable_Low_Temp_Alarm","waspVarValue":"1"},{"waspVarName":"cust_Low_temperature_Hyst","waspVarValue":"36"},{"waspVarName":"sys_valve_exercise","waspVarValue":"0"},{"waspVarName":"sys_pump_exercise","waspVarValue":"0"},{"waspVarName":"sys_supply_diagnostic","waspVarValue":"1"},{"waspVarName":"sys_autobalance","waspVarValue":"1"},{"waspVarName":"sys_pump_management","waspVarValue":"0"},{"waspVarName":"sys_rh_control_activation","waspVarValue":"0"},{"waspVarName":"sys_supply_water_activation","waspVarValue":"0"},{"waspVarName":"sys_cooling_available","waspVarValue":"0"},{"waspVarName":"sys_forced_eco_mode","waspVarValue":"0"},{"waspVarName":"sys_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"sys_comm_module_exist","waspVarValue":"1"},{"waspVarName":"sys_time_limit_bypass","waspVarValue":"0"},{"waspVarName":"sys_heat_pump_dynamic_heatcurve","waspVarValue":"0"},{"waspVarName":"sys_heat_pump_response","waspVarValue":"0"},{"waspVarName":"sys_heat_pump_defrost","waspVarValue":"0"},{"waspVarName":"sys_heat_cool_master_switch","waspVarValue":"0"},{"waspVarName":"Sys_CeilingCooling_Type","waspVarValue":"0"},{"waspVarName":"sys_HC_supply_limit","waspVarValue":"644"},{"waspVarName":"sys_HC_supply_hyst","waspVarValue":"72"},{"waspVarName":"sys_first_stage_offset","waspVarValue":"36"},{"waspVarName":"sys_day","waspVarValue":"3"},{"waspVarName":"sys_Month","waspVarValue":"8"},{"waspVarName":"sys_year","waspVarValue":"24"},{"waspVarName":"sys_minutes","waspVarValue":"16"},{"waspVarName":"sys_hour","waspVarValue":"4"},{"waspVarName":"sys_days","waspVarValue":"1"},{"waspVarName":"sys_seconds","waspVarValue":"30"},{"waspVarName":"Sys_ext_outdoor_temp","waspVarValue":"32767"},{"waspVarName":"sys_heat_cool_offset","waspVarValue":"36"},{"waspVarName":"sys_eco_mode_offset","waspVarValue":"72"},{"waspVarName":"sys_indoor_temp_switch","waspVarValue":"788"},{"waspVarName":"sys_outdoor_temp_hyst","waspVarValue":"36"},{"waspVarName":"sys_outdoor_temp_switch","waspVarValue":"824"},{"waspVarName":"sys_indoor_temp_hyst","waspVarValue":"72"},{"waspVarName":"sys_indoor_temp_delay","waspVarValue":"24"},{"waspVarName":"sys_pun_protocol_version","waspVarValue":"0"},{"waspVarName":"sys_OTA_status","waspVarValue":"3"},{"waspVarName":"sys_controller_1_presence","waspVarValue":"1"},{"waspVarName":"sys_controller_2_presence","waspVarValue":"0"},{"waspVarName":"sys_controller_3_presence","waspVarValue":"0"},{"waspVarName":"sys_controller_4_presence","waspVarValue":"0"},{"waspVarName":"sys_controller_1_lost","waspVarValue":"0"},{"waspVarName":"sys_controller_2_lost","waspVarValue":"0"},{"waspVarName":"sys_controller_3_lost","waspVarValue":"0"},{"waspVarName":"sys_controller_4_lost","waspVarValue":"0"},{"waspVarName":"sys_average_relative_humidity","waspVarValue":"0"},{"waspVarName":"C1_channel_1_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_2_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_3_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_4_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_5_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_6_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_7_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_8_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_9_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_10_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_11_fancoil","waspVarValue":"0"},{"waspVarName":"C1_channel_12_fancoil","waspVarValue":"0"},{"waspVarName":"C1_out_relay_heat_cool_SwFunct","waspVarValue":"0"},{"waspVarName":"C1_general_purpose_input","waspVarValue":"3"},{"waspVarName":"C1_output_module_configuration","waspVarValue":"3"},{"waspVarName":"C1_controller_relays_config","waspVarValue":"3"},{"waspVarName":"C1_channel_1_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_2_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_3_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_4_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_5_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_6_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_7_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_8_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_9_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_10_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_11_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_12_ceiling_cooling","waspVarValue":"0"},{"waspVarName":"C1_channel_1_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_2_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_3_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_4_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_5_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_6_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_7_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_8_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_9_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_10_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_11_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_channel_12_ave_temp","waspVarValue":"1"},{"waspVarName":"C1_rh_dead_zone","waspVarValue":"5"},{"waspVarName":"C1_rh_worst","waspVarValue":"0"},{"waspVarName":"C1_sw_version","waspVarValue":"289"},{"waspVarName":"C1_thermostat_1_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_2_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_3_presence","waspVarValue":"0"},{"waspVarName":"C1_thermostat_4_presence","waspVarValue":"0"},{"waspVarName":"C1_thermostat_5_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_6_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_7_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_8_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_9_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_10_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_11_presence","waspVarValue":"1"},{"waspVarName":"C1_thermostat_12_presence","waspVarValue":"0"},{"waspVarName":"C1_output_module_presence","waspVarValue":"0"},{"waspVarName":"C1_outdoor_temp_sensor_presence","waspVarValue":"0"},{"waspVarName":"C1_heat_cool_presence","waspVarValue":"0"},{"waspVarName":"C1_eco_mode_presence","waspVarValue":"0"},{"waspVarName":"C1_stat_pump_relay","waspVarValue":"0"},{"waspVarName":"C1_stat_supply_temp_hi_alarm","waspVarValue":"0"},{"waspVarName":"C1_stat_supply_temp_low_alarm","waspVarValue":"0"},{"waspVarName":"C1_eco_mode_forced_pub_thermo","waspVarValue":"0"},{"waspVarName":"C1_stat_demand","waspVarValue":"0"},{"waspVarName":"C1_stat_general_system_alarm","waspVarValue":"0"},{"waspVarName":"C1_device_system_alarm_eco_loss","waspVarValue":"0"},{"waspVarName":"C1_stat_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_stat_heat_cool_slave_input","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_1","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_2","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_3","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_4","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_5","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_6","waspVarValue":"1"},{"waspVarName":"C1_thermostat_change_7","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_8","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_9","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_10","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_11","waspVarValue":"0"},{"waspVarName":"C1_thermostat_change_12","waspVarValue":"0"},{"waspVarName":"C1_average_room_temperature","waspVarValue":"727"},{"waspVarName":"C1_average_setpoint","waspVarValue":"32767"},{"waspVarName":"C1_outdoor_temperature","waspVarValue":"32767"},{"waspVarName":"C1_alarm_type","waspVarValue":"0"},{"waspVarName":"C1_supply_temperature","waspVarValue":"32767"},{"waspVarName":"C1_worst_room_temperature","waspVarValue":"32767"},{"waspVarName":"C1_worst_setpoint","waspVarValue":"32767"},{"waspVarName":"C1_stat_heat_pump_dyn_heat","waspVarValue":"0"},{"waspVarName":"C1_hardware_type","waspVarValue":"1"},{"waspVarName":"C1_memory_map","waspVarValue":"1"},{"waspVarName":"C1_out_module_relay1_cmd","waspVarValue":"0"},{"waspVarName":"C1_out_module_relay2_cmd","waspVarValue":"0"},{"waspVarName":"C1_stat_out_module_relay1","waspVarValue":"0"},{"waspVarName":"C1_stat_out_module_relay2","waspVarValue":"0"},{"waspVarName":"C1_stat_out_module_com_lost","waspVarValue":"0"},{"waspVarName":"C1_pending_sw_version","waspVarValue":"279"},{"waspVarName":"C1_bootloader_sw_version","waspVarValue":"1044"},{"waspVarName":"C1_T1_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T2_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T5_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T6_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T7_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T8_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T9_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T10_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T11_bypass_enable","waspVarValue":"0"},{"waspVarName":"C1_T1_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T2_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T5_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T6_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T7_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T8_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T9_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T10_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T11_manual_fan_on","waspVarValue":"0"},{"waspVarName":"C1_T1_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T2_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T5_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T6_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T7_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T8_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T9_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T10_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T11_mode_comfort_eco","waspVarValue":"0"},{"waspVarName":"C1_T1_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T2_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T5_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T6_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T7_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T8_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T9_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T10_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T11_dehumidifier_activation","waspVarValue":"0"},{"waspVarName":"C1_T1_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T2_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T5_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T6_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T7_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T8_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T9_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T10_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T11_rh_control","waspVarValue":"0"},{"waspVarName":"C1_T1_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T2_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T5_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T6_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T7_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T8_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T9_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T10_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T11_eco_profile_number","waspVarValue":"0"},{"waspVarName":"C1_T1_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T2_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T5_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T6_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T7_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T8_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T9_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T10_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T11_pub_setpoint_override","waspVarValue":"0"},{"waspVarName":"C1_T1_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T2_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T5_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T6_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T7_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T8_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T9_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T10_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T11_cooling_allowed","waspVarValue":"1"},{"waspVarName":"C1_T1_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T2_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T5_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T6_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T7_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T8_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T9_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T10_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T11_rh_setpoint","waspVarValue":"75"},{"waspVarName":"C1_T1_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T2_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T5_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T6_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T7_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T8_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T9_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T10_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T11_comfort_heating_setpoint","waspVarValue":"0"},{"waspVarName":"C1_T1_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T2_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T5_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T6_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T7_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T8_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T9_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T10_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T11_minimum_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T1_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T2_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T5_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T6_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T7_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T8_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T9_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T10_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T11_maximum_setpoint","waspVarValue":"950"},{"waspVarName":"C1_T1_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T2_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T5_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T6_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T7_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T8_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T9_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T10_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T11_minimum_floor_setpoint","waspVarValue":"680"},{"waspVarName":"C1_T1_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T2_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T5_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T6_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T7_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T8_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T9_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T10_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T11_maximum_floor_setpoint","waspVarValue":"788"},{"waspVarName":"C1_T1_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T2_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T5_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T6_setpoint","waspVarValue":"725"},{"waspVarName":"C1_T7_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T8_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T9_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T10_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T11_setpoint","waspVarValue":"410"},{"waspVarName":"C1_T1_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T2_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T5_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T6_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T7_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T8_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T9_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T10_eco_offset","waspVarValue":"72"},{"waspVarName":"C1_T11_eco_offset","waspVarValue":"72"},
DEL 2
{"waspVarName":"C1_T1_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T2_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T5_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T6_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T7_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T8_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T9_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T10_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T11_stat_cb_wifi_installed","waspVarValue":"1"},{"waspVarName":"C1_T1_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_need_date_info","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_eco_forced","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_sub_actuator","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_actuator","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_rh_cool_shutdown","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_floor_limit_reach","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_fallbk_heatalarm","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_holiday_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_cb_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_air_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_external_sensor_err","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_rh_sensor_error","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_comfort_eco_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_tamper_alarm","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_rf_error","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_battery_error","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_rf_low_sig_warning","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_valve_position_err","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_eco_program","waspVarValue":"0"},{"waspVarName":"C1_T1_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T2_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T5_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T6_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T7_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T8_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T9_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T10_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T11_stat_demand_led","waspVarValue":"0"},{"waspVarName":"C1_T1_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T2_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T5_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T6_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T7_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T8_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T9_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T10_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T11_thermostat_type","waspVarValue":"2"},{"waspVarName":"C1_T1_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T2_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T5_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T6_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T7_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T8_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T9_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T10_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T11_eco_setting","waspVarValue":"0"},{"waspVarName":"C1_T1_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T2_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T5_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T6_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T7_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T8_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T9_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T10_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T11_system_device_public","waspVarValue":"0"},{"waspVarName":"C1_T1_input_state","waspVarValue":"0"},{"waspVarName":"C1_T2_input_state","waspVarValue":"0"},{"waspVarName":"C1_T5_input_state","waspVarValue":"0"},{"waspVarName":"C1_T6_input_state","waspVarValue":"0"},{"waspVarName":"C1_T7_input_state","waspVarValue":"0"},{"waspVarName":"C1_T8_input_state","waspVarValue":"0"},{"waspVarName":"C1_T9_input_state","waspVarValue":"0"},{"waspVarName":"C1_T10_input_state","waspVarValue":"0"},{"waspVarName":"C1_T11_input_state","waspVarValue":"0"},{"waspVarName":"C1_T1_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T2_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T5_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T6_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T7_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T8_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T9_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T10_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T11_sensor_only","waspVarValue":"0"},{"waspVarName":"C1_T1_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_regulation_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T2_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T5_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T6_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T7_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T8_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T9_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T10_cool_allowed","waspVarValue":"1"},{"waspVarName":"C1_T11_cool_allowed","waspVarValue":"1"},
DEL 3
{"waspVarName":"C1_T1_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T2_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T5_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T6_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T7_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T8_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T9_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T10_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T11_manual_cool_allowed","waspVarValue":"0"},{"waspVarName":"C1_T1_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T2_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T5_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T6_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T7_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T8_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T9_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T10_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T11_heat_cool_mode","waspVarValue":"0"},{"waspVarName":"C1_T1_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T2_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T5_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T6_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T7_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T8_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T9_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T10_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T11_heat_cool_slave","waspVarValue":"0"},{"waspVarName":"C1_T1_room_temperature","waspVarValue":"786"},{"waspVarName":"C1_T2_room_temperature","waspVarValue":"736"},{"waspVarName":"C1_T5_room_temperature","waspVarValue":"694"},{"waspVarName":"C1_T6_room_temperature","waspVarValue":"722"},{"waspVarName":"C1_T7_room_temperature","waspVarValue":"703"},{"waspVarName":"C1_T8_room_temperature","waspVarValue":"694"},{"waspVarName":"C1_T9_room_temperature","waspVarValue":"751"},{"waspVarName":"C1_T10_room_temperature","waspVarValue":"738"},{"waspVarName":"C1_T11_room_temperature","waspVarValue":"702"},{"waspVarName":"C1_T1_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T2_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T5_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T6_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T7_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T8_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T9_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T10_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T11_external_temperature","waspVarValue":"32767"},{"waspVarName":"C1_T1_rh","waspVarValue":"43"},{"waspVarName":"C1_T2_rh","waspVarValue":"48"},{"waspVarName":"C1_T5_rh","waspVarValue":"57"},{"waspVarName":"C1_T6_rh","waspVarValue":"51"},{"waspVarName":"C1_T7_rh","waspVarValue":"54"},{"waspVarName":"C1_T8_rh","waspVarValue":"54"},{"waspVarName":"C1_T9_rh","waspVarValue":"47"},{"waspVarName":"C1_T10_rh","waspVarValue":"50"},{"waspVarName":"C1_T11_rh","waspVarValue":"56"},{"waspVarName":"C1_T1_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T2_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T5_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T6_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T7_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T8_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T9_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T10_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T11_hw_type","waspVarValue":"7"},{"waspVarName":"C1_T1_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T2_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T5_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T6_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T7_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T8_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T9_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T10_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T11_sw_version","waspVarValue":"12"},{"waspVarName":"C1_T1_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T2_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T5_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T6_ufh_pwm_output","waspVarValue":"15"},{"waspVarName":"C1_T7_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T8_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T9_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T10_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T11_ufh_pwm_output","waspVarValue":"50"},{"waspVarName":"C1_T1_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T2_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T5_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T6_head1_supply_temp","waspVarValue":"15"},{"waspVarName":"C1_T7_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T8_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T9_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T10_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T11_head1_supply_temp","waspVarValue":"50"},{"waspVarName":"C1_T1_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T2_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T5_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T6_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T7_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T8_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T9_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T10_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T11_head1_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T1_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T2_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T5_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T6_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T7_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T8_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T9_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T10_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T11_head1_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T1_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T2_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T5_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T6_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T7_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T8_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T9_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T10_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T11_head1_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T1_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T2_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T5_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T6_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T7_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T8_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T9_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T10_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T11_ufh1_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T1_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T2_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T5_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T6_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T7_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T8_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T9_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T10_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T11_head2_valve_pos_percent","waspVarValue":"0"},{"waspVarName":"C1_T1_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T2_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T5_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T6_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T7_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T8_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T9_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T10_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T11_head2_valve_pos","waspVarValue":"0"},{"waspVarName":"C1_T1_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T2_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T5_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T6_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T7_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T8_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T9_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T10_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T11_head2_sw_version","waspVarValue":"0"},{"waspVarName":"C1_T1_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T2_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T5_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T6_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T7_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T8_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T9_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T10_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T11_ufh2_actuator_cycle","waspVarValue":"0"},{"waspVarName":"C1_T1_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T2_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T5_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T6_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T7_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T8_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T9_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T10_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T11_head2_supply_temp","waspVarValue":"0"},{"waspVarName":"C1_T1_channel_position","waspVarValue":"11"},{"waspVarName":"C1_T2_channel_position","waspVarValue":"12"},{"waspVarName":"C1_T5_channel_position","waspVarValue":"18"},{"waspVarName":"C1_T6_channel_position","waspVarValue":"36"},{"waspVarName":"C1_T7_channel_position","waspVarValue":"67"},{"waspVarName":"C1_T8_channel_position","waspVarValue":"198"},{"waspVarName":"C1_T9_channel_position","waspVarValue":"286"},{"waspVarName":"C1_T10_channel_position","waspVarValue":"511"},{"waspVarName":"C1_T11_channel_position","waspVarValue":"1214"},{"waspVarName":"C1_T1_head_number","waspVarValue":"0"},{"waspVarName":"C1_T2_head_number","waspVarValue":"0"},{"waspVarName":"C1_T5_head_number","waspVarValue":"0"},{"waspVarName":"C1_T6_head_number","waspVarValue":"0"},{"waspVarName":"C1_T7_head_number","waspVarValue":"0"},{"waspVarName":"C1_T8_head_number","waspVarValue":"0"},{"waspVarName":"C1_T9_head_number","waspVarValue":"0"},{"waspVarName":"C1_T10_head_number","waspVarValue":"0"},{"waspVarName":"C1_T11_head_number","waspVarValue":"0"},{"waspVarName":"C1_id_output_module","waspVarValue":"0"},{"waspVarName":"C1_id_sys_dev_outdoor","waspVarValue":"0"},{"waspVarName":"C1_id_sys_dev_hc","waspVarValue":"0"},{"waspVarName":"C1_id_sys_dev_eco","waspVarValue":"0"},{"waspVarName":"C1_thermostat1_id","waspVarValue":"285961876"},{"waspVarName":"C1_thermostat2_id","waspVarValue":"285995770"},{"waspVarName":"C1_thermostat3_id","waspVarValue":"285965870"},{"waspVarName":"C1_thermostat4_id","waspVarValue":"285645770"},{"waspVarName":"C1_thermostat5_id","waspVarValue":"282587029"},{"waspVarName":"C1_thermostat6_id","waspVarValue":"285254961"},{"waspVarName":"C1_thermostat7_id","waspVarValue":"282587403"},{"waspVarName":"C1_thermostat8_id","waspVarValue":"286584474"},{"waspVarName":"C1_thermostat9_id","waspVarValue":"286852145"},{"waspVarName":"C1_thermostat10_id","waspVarValue":"28685845"},{"waspVarName":"C1_thermostat11_id","waspVarValue":"28352483"},{"waspVarName":"C1_thermostat12_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_1_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_2_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_3_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_4_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_5_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_6_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_7_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_8_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_9_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_10_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_11_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_12_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_13_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_14_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_15_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_16_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_17_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_18_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_19_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_20_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_21_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_22_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_23_id","waspVarValue":"0"},{"waspVarName":"C1_TTH_24_id","waspVarValue":"0"},{"waspVarName":"controller1_id","waspVarValue":"412584452"},{"waspVarName":"controller2_id","waspVarValue":"0"},{"waspVarName":"controller3_id","waspVarValue":"0"},{"waspVarName":"controller4_id","waspVarValue":"0"},{"waspVarName":"C1_T1_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Monday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Monday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Tuesday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Tuesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Wednesday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Wednesday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Thursday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Thursday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Friday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Friday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Saturday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Saturday","waspVarValue":"000000000000"},{"waspVarName":"C1_T1_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T2_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T5_Sunday","waspVarValue":"000fffffffff"},{"waspVarName":"C1_T6_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T7_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T8_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T9_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T10_Sunday","waspVarValue":"000000000000"},{"waspVarName":"C1_T11_Sunday","waspVarValue":"000000000000"}]}}
I have published a new release that resolves some reported bugs and crashes. Now that the app is mostly stable I will look into some of the feature requests.
Hi Chris! Thank you so much for making this app!! Have been looking this since even before our neely built apartment was finished, gave up for a while and finally found this, thanks!
Here, auto-discovery did not work but entering the ip-address of the module (I have it hard-wored with a fixed IP) did the trick!
Hi Chris
After the latest update v0.0.10 I have problems connecting to the thermostats. Every minute it changes which thermostat it has contact with. In v0.0.8 it worked best for me, as long as I didn’t restart Homey. If Homey was reset, I had to delete and add the thermostats that I couldn’t connect to. Have tried with fixed IP
@orda1 I have just released a patch that increases the network timeout from 3 to 30 seconds. This should help for users with a larger amount of devices like you.
For everyone experiencing problems with thermostats randomly going offline or having memory issues, here’s what I wrote on GitHub earlier:
Currently the architecture of the app creates an API call for every added Homey device. For larger number of thermostats this might lead to issues with memory, either in Homey or on the Uponor control unit. I have started a rewrite to follow the architecture of my other app (Remeha Home) to only do a single API call for all devices (from the “driver” part of the Homey app) and have the devices pull the data from the driver. This should reduce network calls for every use, increase network performance for larger installations and hopefully mitigate the memory issues. It might take a few weeks to complete and test this rewrite.
Thanks for your patience!
Hi everyone,
After several weeks of testing I have now released version 0.1.0 to the testing channel (Uponor Smatrix App for Homey | Homey). This is a complete rewrite of the networking and discovery logic, so please only install this test release if you are comfortable with the occasional issue. Hopefully several people can validate that this rewrite reduces the networking issues previously reported, and I can make this release available to everyone.
Please note that settings for the IP address and debug information have been moved from the device settings to the app settings page.
Thanks for testing!
Chris
Substantial improvement on sensor stability after the last update, great work!
Some "nice-to-have"s I’ve picked up for consideration on future developments:
  • Read Eco modus and temperature. Currently the temperature show the standard set temperature even though Eco is active. Context: I use Eco on bedrooms to control night/day and weekday/weekend differentiation. (think this one has been mentioned before on the forum)
  • Control/Set Eco modus/profile per room. Figure this may be a bit complicated the way Uponor is handling Eco though
  • Read floor sensor temperature. Potentially also set min/max floor temperature.
  • Add flow to lower/raise temperature with X degrees
@Orjanfos Thanks for confirming that the app is more stable for you!
Regarding your suggestions:
  • The eco temperature is available in the API, so this shouldn’t be a problem. However Homey as a certain standard of which data to mark as target temperature, which is then shown in the UI tiles. Not sure if a deviation from this will pass the app review.
  • Not sure if I can enable/disable eco modus per thermostat zone. Let me check the API.
  • Can you send me your debug data (from the app settings menu) so I can see what floor sensor temperature look sl ike in the API? I don’t have a system with this sensor so it’s hard to test.
  • Homey’s standard UI for thermostats only allows increasing/decreasing per 0.5 degrees. Better to file a question with Athom to add more options there.
Chris
Hi everyone!
I have read everything in this topic but I still can’t add my thermostats. The automatic search doesn’t find them nor does it work when I enter the IP adress for my home WiFi. Does anyone have any tips on where to start troubleshooting? Anyone else with problem finding the units?
Andreas
Hi, have the same problem, how did it work out for you?
Ralf
Hi!
Nothing yet. Everytime I try to add a new device with IP adress, the same message appears: “No new units have been found”. And it appears instantly. Almost as if it doesn’t actually do the search.
How about you? Any luck?