How to switch Fibaro plug when power uage is bigger than - 800 W

Which flow must I use when I want to trigger a Fibaro plug when my power usage is more than -800 W. So if the total power usage is - 800 W or more, due to my solarpanels, I want to trigger a Fibaro plug to on. I have a P1 meter from Honewizard.
I tried the flow in the picture, but it does not seems to work.

“or less”

The flow triggers when the value changes from a value higher than -800, to a value less than -800.
When the value changes, but stays anywhere below -800, the flow won’t trigger.

I suggest to add a timeline notification card, with the power tag added to it, to see what happens

I am struggeling with the term higher or lower. I want to trigger the plug when I deliver more than 800 watt back to the grid. My current flow is in Dutch, so it says (kleiner) which is lower than - 800 W, or should I use (groter) higher than - 800 W

-1000 is smaller / less than -800
-400 is higher / more than -800

So to me your flow trigger is OK.