[APP][Pro&Cloud][OFFICIAL] SolarEdge - Powering People’s Lives Around the World

Login was successful, but I am no longer receiving any updates.
I do not use two-factor authentication (2FA).

Here is the diagnostic report code: 4e8c117f-43f7-4dde-a600-960a9896f71d

Could you please help me identify and resolve this issue?
I really appreciate your effort you put into this app, many compliments for your commitment!

Sadly still doesn’t work for me on 2.1.2 , just received this update today

UPDATE: it looks like new data is retrieved again! I haven’t changed anything, so a bit strange. My version 2.1.2

Keep you posted.

Hi everyone,

First of all, thank you for the recent update of the SolarEdge app and for all the work that goes into it. Everything else has been running smoothly since the update, so I really appreciate the effort.

I’ve noticed one issue in the Homey Energy section, though. Since the update, the house consumption (“Hausverbrauch”) is no longer displayed correctly. Instead, Energy now shows either the power (“Leistung”) or the grid power (“Netzleistung”) value, which is not correct. Before the update, the house consumption was shown there as expected.

Is this a known issue, or is there a setting I may have missed after the update?

Thanks a lot in advance for your help!

Best regards,
René

I have also tried connecting all devices via Modbus. Everything works fine there as well, except for the inverter: it shows an incorrect solar power value, for example around 1800 W instead of 300 W. The 300 W is the correct value, as confirmed both by the device connected via the cloud and by the official SolarEdge app.

Hi Robin, thanks for taking the app on and adding the Modbus drivers. I’ve been testing Inverter (Modbus), Battery (Modbus) and Meter (Modbus) on app v2.1.2 since 22 Oct, alongside the older SolarEdge + Growatt app for comparison. The meter and battery look great. I’ve found one issue on DC-coupled systems, and I have two requests.

Setup: a SolarEdge inverter with a DC-coupled SolarEdge battery and a SolarEdge Modbus meter, on Homey Pro (Early 2023). No backup interface.

1. Inverter (Modbus) power is AC output, so on a DC-coupled system it isn’t PV generation

Inverter (Modbus) measure_power is the inverter’s AC power, and meter_power is its lifetime AC energy. With a DC-coupled battery, that AC figure includes whatever the battery is doing. From my Insights, using the app’s own Battery (Modbus) readings:

Time Inverter (Modbus) Battery (Modbus) Actual PV
22 Oct 12:40, charging from PV ~300 W +1,770 W ~2.1 kW
22 Oct 12:49, battery idle 1,644 W 0 W 1,644 W
23 Oct 03:00, charging from grid −4,936 W +4,900 W ~0 W
23 Oct 16:50, discharging at peak ~+4,990 W −5,000 W ~0 W

So PV ≈ inverter AC power + battery power (battery positive when charging). The small negative remainder while grid-charging is conversion losses.

The inverter is solarpanel class, so Homey Energy takes this as solar generation. Including it in Energy would:

  • show about 5 kW of “solar” at dusk while the battery discharges, as well as the battery discharging, so the discharge is counted twice;
  • miss solar that goes straight into the battery;
  • show negative solar overnight, which the SDK says Homey treats as consumption.

I noticed your cloud inverter driver already handles this. It adds the battery to the AC power for DC-coupled sites, so for now I’m keeping the cloud inverter as my Energy solar source.

Request: could Inverter (Modbus) report PV the same way the cloud driver does, by adding the battery’s power whenever the inverter has a DC-coupled battery? The app can detect one from the battery registers, as the battery driver already does when pairing, whether or not a Battery (Modbus) device is paired. Without a battery the battery term is zero, so nothing changes for anyone else.

  • measure_power = AC power + battery power, clamped at 0.
  • meter_power = cumulative PV energy. I don’t think the registers give PV energy directly: the AC energy counter only counts production and stays flat while charging from the grid. The app would probably need to integrate PV power itself and keep the total in the device store.
  • The raw AC readings could move to sub-capabilities, for example measure_power.ac and meter_power.ac, for anyone who wants them.

That would make the three Modbus devices a complete, fully local Homey Energy setup for DC-coupled installations.

2. Small request: one decimal on battery SoC

Battery (Modbus) measure_battery is rounded to whole percent: 92 when the other app showed 91.46. The register is a float, so one decimal would help flows with thresholds near 100%.

3. Request: charge and discharge limit controls on Battery (Modbus)

My battery automation relies on one SolarEdge behaviour: self-consumption with the discharge limit set to 0 W. Solar can still charge the battery, but it doesn’t discharge into the house. I hold the battery like that every day until the evening peak, and in the evening before grid events. I currently write the remote-control charge and discharge limit registers with the older app.

The new modes don’t seem to cover this. Homey mode at 0 W idles the battery, which also stops solar charging it. Your source notes the backup reserve only applies with backup hardware, which my inverter doesn’t have, so it can’t be used as a floor either.

Could Battery (Modbus) expose the charge and discharge limits, for example as action cards “Set discharge limit to … W” and “Set charge limit to … W”? That would let me retire the older app completely.

Happy to test a build, send a diagnostics report, or share more Insights data. Thanks again!

yes, will be implemented in next release. Note that indeed during battery activity the PV power on AC side is an estimate due to unknown inverter losses.

yes, will be implemented in next release

yes, will be implemented in next release. Also a new standard battery mode ‘pv_charge_only’ will be added.

will be fixed. see previous reply

This is not a bug. It is actually the v2 SolarEdge app now complying to Homey Energy standards. Just rename your device called ‘Hausverbrauch’ to ‘Netz’, because that is what that meter represents now. Your in-house use is derived by Homey Energy based on that.

v2.2.0 is ready for testing:

  • Added Modbus battery charge and discharge limits
  • Added PV charge only mode
  • Fixed Modbus PV power during battery activity
  • Improved polling of multiple inverters
  • Minor other fixes and improvements

Hi Robin, thanks for the quick test build. I installed 2.2.0 - here’s what I found:.

1. PV on Inverter (Modbus): looks right so far. With the battery idle it matches the cloud inverter (322 W against 320 W), and the AC readings on the new sub-capabilities match what the main reading used to show. I’ll confirm through a peak discharge and an overnight grid charge, which are the real tests, and report back.

2. SoC to one decimal: working, thanks.

3. The Homey-run modes are refused on my inverter. Setting the target power mode to Force discharge fails straight away with “Remote battery control needs advanced power control in the inverter (0xF142 = 1, 0xF104 = 4); ask your installer.” Nothing is written. Export limitation is also on, with a 500 W site limit (0xE002), so I’d hit that check next. The app’s “Set export limit” control accepts writes, so the mode bits in 0xE000 must be set.

But remote control works on this inverter as it is configured now. I run it every day with another app:

  • Storage Control Mode 4 (Remote Control).
  • Default modes 3, 4 and 7 (0xE00A).
  • Charge and discharge limits (0xE00E and 0xE010).

The battery exports at about 5 kW through the evening peak in Maximize export. So on my system neither setting stops storage remote control.

My understanding is that advanced power control applies to the active and reactive power limiting registers rather than the storage-control block. Is that right? Either way, could these checks become warnings, or a device setting that lets the user override them? I’d rather not change grid settings on the inverter given it has been working as-is.

4. Two questions on Charge from solar only.

  • What it charges from. It sends remote command 1. As I read the Power Control document, command 1 charges only from PV the inverter can’t put out as AC (above its AC power limit), not from surplus over house load. Is the mode meant to charge from the surplus, and have you seen it do that on a real system?
  • The daily hold. The behaviour I hold the battery in every day is Maximize self-consumption (command 7) with the discharge limit at 0 W. Solar charges the battery from the surplus, but it doesn’t discharge. Could there be a Homey-run self-consumption mode (command 7) that respects the maximum discharge power card? With that, and the point above resolved, I could retire the other app completely.

Happy to test further builds. Thanks again!

When i switch from cloud connection to modbus will all past solar data be lost or is there a way to save the data?

It is not a switch. You will add a new modbus based device, and your existing cloud based devices will stay until you delete it manually.

Yes, I understand, but what I meant is: if I add the device via Modbus and delete the cloud-based one, will I lose all my past solar data in the Energy tab?

Dont think so. But that would be a question for the developer of the Energy tab (Athom).

Hi @RM_de_Gruijter

A follow-up on remote control: as I mentioned on 25 Oct, the app refuses the Homey-run modes on my inverter because advanced power control is off and export limitation is on (500 W site limit). I understand why, given SolarEdge’s Power Control document. But on this inverter remote control does work as configured: the SolarEdge + Growatt app has run it daily for months (Storage Control Mode 4, default modes 3/4/7, charge and discharge limits), including about 5 kW exports at the evening peak.

So I’m testing a small opt-in on a fork: a battery-device setting, off by default, that turns the pre-check into a warning instead of a refusal. The app would still never write the advanced power control or export limitation registers. I’m running supervised sessions on my inverter and recording each command with your capture tooling, plus before-and-after reads of 0xE000, 0xE002, 0xF142 and 0xF104 to show nothing else changes.

If it holds up, would you consider a pull request along those lines? Or if you’d rather handle it differently, or there’s a reason the rule matters that I’m missing, let me know and I’ll adapt or hold off.

I currently have both this app and SolarEdge + Growatt TCP modbus | Homey running in parallel with the latter handling control, and I’m trying to reduce down to just yours.

Thanks in advance!
Jon

Thanks Jon!

Support will be built into the next app release, so no PR needed.

  • Advanced power control off: remote control now runs, with a warning on the device.
  • New battery setting Ignore export limitation, off by default. When on, export can exceed your site limit.

Could you tell me the values of 0xF142 and 0xF104? And were the 5 kW exports measured at the grid meter?

new version 2.2.1 is ready for testing:

  • Battery control also works without advanced power control
  • Added setting to ignore export limitation
  • The battery returns to its previous mode after Homey control
  • Improved Modbus discovery

please test @Jonathan_Draper

Thanks Robin, that’s great news, and much simpler than a PR.

I see you’ve already published the new version, thanks! I’m installing it now and will report back how it behaves here. Meanwhile, here are the details you asked for, which may matter for the new settings:

Inverter: SE5000H, 5,000 W rated, single phase, firmware 0004.0024.0014. The app shows its power limit control as “Basic”.

Registers, read today over Modbus:

  • 0xF142 = 1 (advanced power control enabled)
  • 0xF104 = 0
  • 0xE000 = 2049, 0xE001 = 0, 0xE002 = 500.0 W (float32, low word first)

Two corrections to what I told you earlier, sorry. Advanced power control is on: only F104 differs from what the app checks for (4). And 2049 in 0xE000 looks like Minimum Import Control, not export limitation (the SolarEdge + Growatt app writes 2049 for its “Minimum Import Control” option), so the 500 W is a minimum import setting. The app’s check reads bits 0–2 of 0xE000, so it treats this as export limitation. Is that intended?

The exports: the 5 kW I mentioned is the battery’s discharge, not the grid export. At the grid, the sustained export at the evening peak is 3.8–3.9 kW (best 10-minute average each day for the last week), and the SolarEdge meter and my supplier’s smart meter agree to within about 10 W. Single readings peak at around 4.4–4.7 kW.

The grid export stays at 3.8–3.9 kW while the battery’s discharge varies between 4.2 and 4.9 kW, so something caps it. 3.9 kW is exactly 78% of the inverter’s rating, and the SolarEdge + Growatt app’s active power limit reading sits at 78–90% while the battery exports and barely moves otherwise. None of my Homey flows writes it, so the cap may be the active power limit rather than any export setting. Would “Ignore export limitation” affect that?

For what it’s worth, my DNO consent allows export up to 32 A per phase, so neither the ~3.9 kW cap nor the 500 W minimum import is a grid requirement here.

Thanks Jon!

2049 is export limitation with a minimum import (SolarEdge’s document), so keep Ignore export limitation on.
The warning on the device follows SolarEdge’s official document (0xF104 = 4); you can ignore it, since your inverter shows it works without.