[APP][Pro] Luxtronik Heat Pump Manager – Control and monitor your Luxtronik heat pump

Hi Andi,

I am running 2.0.50 and auto update is on.
It also does not seem to actually toggle the cooling on/off via the app. It does not push to the device.

I have a fixed IP for the device, and i double checked the IP with the MAC.

Hi Ronald,

Thanks for the report

cooling_operation_mode always null: Found it. Firmware V3.x controllers can return values other than 0 or 1 for the cooling mode register (Luxtronik 2.0 only ever uses 0/1). The app passed that unexpected value directly to Homey’s enum capability, which silently rejected it — leaving the value at null permanently. Fixed in 2.0.51.

Write doesn’t push to device: This is separate and I haven’t been able to reproduce it from the code. Could you check the Homey app diagnostics immediately after triggering the Set cooling mode action? I’d like to see whether the write times out, gets a protocol error, or whether the controller acknowledges it but reverts the value on the next read (please submit a diagnostic report).

2.0.51:

Hey Andi,

Tested it all operation mode settings on the device now, including the cooling operation mode. .51 fixes the cooling.

My “does not push to device” was a false statement. It does push to the device, but not to the room thermostat i have.

The heatpump does toggle the cooling mode on/off, but it does not feedback to the thermostat that cooling is turned “off”.

But the pump does stop/start itself on command!

One more question:

I bet there is no way to actually set the room temp in Homey, since that is set on the room controller? Cant find anything in the app currently on this option.

Thanks for the quick fix!

Hi Ronald,

Glad 2.0.51 fixed it!

The thermostat feedback is a hardware limitation — the controller doesn’t signal the RBE when toggled via protocol.

Room temperature reading works if you have a Luxtronik RBE room display connected (the measure_temp_room capability appears automatically). Setting it via Homey isn’t possible — the Luxtronik protocol doesn’t expose a writable register for the room setpoint. The closest you can do is adjust the heating curve correction (±5 °C) which shifts the overall heat output.

Hi Andi, thanks for publishing this app, I have been lookin for it for a long time..

question: the app installs well and connects correctly to my Luxtronik manager (on an Alpha Innotec LWDV, only used for heating, not warm water). I can read all values and can switch the heatpump mode on/off/holiday/party, etc. The only thing that does not work is the temperature correction setting. The flowcard plays correctly on values between +5 and -5 degr but the Luxtronix manager does not take over the setting and remains at ‘0’. A manual setting on the Luxtronik works fine. Any idea how to fix this?

Hi Hans

thanks for the report. The fact that changing the mode works is a really useful clue.
In the app, the mode change and the temperature correction are written in exactly the same way, so the connection itself is fine. The correction goes to the controller setting “Temperatur ±” (parameter 1), the same one the Home Assistant integration uses. The controller confirms that it received the command; otherwise the flow card would show an error. So your controller seems to accept the value without applying it, and I’d like to find out why.

Could you check a few things?

  1. Your firmware version. It’s shown on the firmware tile of the device in Homey.
  2. Run the flow once with, say, +2, then watch the “Heating Correction” tile. Does it show +2 and drop back to 0 after about two minutes?
  3. Right after that, send a diagnostics report from the app’s page (Homey app → More → Apps → Luxtronik Heat Pump Manager) and post the report ID here.
  4. Is a room control unit (RBE) or a remote setpoint adjuster connected to the Luxtronik?
  5. Does the controller show “Please wait” or restart after the flow runs?

Why I’m asking about 1: Alpha Innotec firmware V1.90.0 / V2.90.0 has a known fault exactly here. Values written over the network are either confirmed but not applied, or the controller restarts after every write. Others have reproduced it outside Homey too. If you’re on a .90 version, going back to an older firmware through your installer or Alpha Innotec support has fixed it for other owners.

Hi Andi,

The controller runs firmware version V3.88.0, so that should be OK, I guess. I have explored a bit further:

Regarding the controller and the reported values on the tiles, the following:
The controller-menu offers different ways to change the parallel shift of the heating temperature (all in Dutch, sorry..)
->. In the main menu you can scroll to the +/- button to adjust the shift between +5 and -5 degr (see first picture MainMenu.jpg)
->. From the main menu you can go into the Heating Settings submenu which shows menu options for Heating Curve (“Stooklijnen”) and Temperature (“Temperatuur ±”) (see second picture Heating submenu.jpg)
->. Going into the Temperature submenu you can finetune the heating curve (see third picture Heating submenu Temperature.jpg); I don’t use the finetuning.
->. Going into the Heating Curve submenu you can adjust the temperature parallel shift for the default nighttime reduction (see fourth picture Heating submenu Heatingcurve.jpg) The nighttime interval itself is set in the submenu Heating Settings “Klokprogramma”, I have not set such interval, the pump always runs in daytime mode. According to the manual the nighttime reduction shift is also applied when switching the controller mode to “Holiday”.

It now appears that:

  1. The “Heating Correction” tile in Homey always shows the nighttime reduction shift. Changing the value manually in the Luxtronik controller in the Heating Curve submenu, results in a corresponding change in the tile-value (after the polling interval).
  2. Changing the temperature correction manually in the Main menu does not result in any change of the tile-value. The tile still shows the nighttime reduction shift.
  3. After using the flowchart “Temperature Correction” with any value, nothing happens in the Luxtronik controller menu until you manually toggle once between the Main menu and a submenu and back, after which the Main menu is apparently refreshed and it then shows the value as set with the flowchart. The submenus Heating Settings Temperature and Heating Settings Heatingcurve remain unchanged and the tile still shows the (unchanged) nighttime reduction shift.

So, it seems that the heating correction setting as defined with the flowchart is still correctly recorded by the Luxtronik controller but it only shows up there after manually refreshing the main menu. The “Temperature Reduction” tile in Homey does not show it at any time as it always shows the nighttime reduction temperature (which does not change with the flowchart); I think this caused my confusion…

/Hans

(attachments)




Two quick checks would narrow it down further:

On the controller, set “Temperatuur + −” to +1.0 and confirm with ✓. Wait two minutes and look at the heating correction in Homey. Does it show +1.0? Afterwards, set it back to 0.

The check tells me whether the app reads the same setting the controller panel uses.

here is what happens:

  1. Changing “Temperatuur + -” in the Settings submenu results in a change of the heating curves settings. When changing with 1 degree up and confirming with ✓, the controller says that it will re-calculate the existing heatingcurve setpoints with a 1 degree parallel shift. After confirming again with ✓ the heating curve setpoints are changed and the setting in “Temperatuur + -” is set back to “0”. The tile in Homey does not change.

  2. Changing “Nighttime reduction” temperature in the submenu “Heating Curves” with any change up or down (and confirming with ✓) results in an identical change in the tile in Homey. The “Heating Correction” tile always shows the value of the manually set "Nighttime reduction"in the submenu “Heating Curves”.

  3. Changing the temperature in the controller Home screen (the “+/-” button with the temperature bar below it) results in a physical heating temperature change, but the tile in Homey still shows the “Nighttime reduction” temperature

  4. When using the flowcard “Set Heating Temperature Correction” with any temperature setting results in a change of the reported temperature in the controller Home screen (the temperature bar also indicates the applied change setting). The tile in Homey still shows the “Nighttime reduction” temperature.

in Summary: I can change the heating temperature correction on the controller with a flowcard, but the tile value in Homey will not change and will always show the “Nighttime reduction” temperature that has been manually set in the Luxtronik controller.

Hope this helps.

Thanks Hans, this is exactly what I needed, and it changes the picture.

The flow card does work. Your points 3 and 4 show it: the value you set with the flow card appears in the +/- on the controller’s home screen, and that is the value the heat pump actually heats by. The “Temperatuur + −” entry in the Settings menu is something else on your controller. It shifts the heating curve points once and then returns to 0, so it will always show 0. That’s why it looked as if nothing was taken over.

What is wrong is the tile in Homey. It reads the value back from the controller, and on your controller that read returns the night reduction instead of the home-screen correction. I want to fix that, so I need to find out where your controller keeps the home-screen value.

Version 2.1.12 (install Luxtronik Heat Pump Manager | Homey) adds what I need for that: the Debug tab in the app settings now lists every parameter of the controller. Once you have it, could you do this:

  1. On the controller, set the night reduction (Heating Curves) to -1.5 and the +/- on the home screen to +2.0.
  2. Wait a minute. Then open the app settings in Homey, go to the Debug tab, press Refresh and then Copy Log. Save that text.
  3. Run the flow card “Set heating temperature correction” with +1.0. Note what the night reduction row and the home screen +/- show on the controller.
  4. Wait a minute, then Refresh and Copy Log again.

Please send me both texts and your notes from step 3 as a private message rather than posting them here, because the log contains your heat pump’s serial number and network addresses. Afterwards you can set everything back to your own values.