[APP][Pro] Remeha Modbus - Monitor and control your Remeha heat pump via Modbus TCP
Hello there,
Update 19 April 2026: v1.1.0 is now in test. See the post below for
the install link and what’s changed. The description below covers
the current stable version (v1.0.2).
I’ve developed a Homey App that connects your Remeha heat pump directly to Homey over your local network using Modbus TCP. It polls the heat pump’s registers in real-time via the GTW-08 service gateway, giving you full monitoring and control from Homey dashboards and Flows.
Note: NO cloud, direct local Modbus TCP communication.
Remeha Modbus
This Homey app connects to a Remeha heat pump through the local network using Modbus TCP and retrieves real-time operating data. It allows you to monitor temperatures, pressures, energy consumption and COP directly from your Homey smart home system. Using Flows you can send commands to the heat pump to change thermostat mode, DHW comfort setpoint, silent mode, hybrid mode and tariffs.
FEATURES
When a device is added and communication is working, the device will display various statistics such as:
  • Room, flow, return, outdoor and heat pump temperatures
  • Water pressure and flow rate
  • System status (standby, heating, heat pump, hybrid, defrost, error)
  • Tap water (DHW) active indicator
  • COP (Coefficient of Performance)
  • Pump speed
  • Compressor starts and operating hours
  • Total energy consumption (kWh)
  • DHW energy consumption (kWh)
  • CH energy delivery (kWh)
  • DHW energy delivery (kWh)
  • Boiler energy consumption and delivery (kWh)
You can also send commands to the heat pump through Homey Flows (‘Then…’):
  • Thermostat mode (auto / heat / off)
  • Room temperature setpoint
  • DHW comfort setpoint and on/off
  • Silent mode with schedule
  • Hybrid mode (auto / heat pump only / boiler only)
  • Electricity and gas tariffs
  • Push live power (W) and energy (kWh) readings from any external meter
REQUIREMENTS
This app requires Homey Pro or Homey Pro Mini (firmware 13.0.0 or newer) and a Remeha heat pump with the following hardware setup:
  • Remeha GTW-08 gateway connected to the service connector on your heat pump
  • RS485 to Ethernet converter (e.g. Waveshare RS485 TO ETH (B)) to bridge the GTW-08’s Modbus RTU (RS485) to Modbus TCP on your local network
Supported models:
  • Elga Ace Hybride Split (indoor unit)
  • Elga Ace Monoblock (outdoor unit)
  • Elga All-in-One Hybrid (indoor combined unit)
HARDWARE SETUP
Remeha Heat Pump → GTW-08 (service connector) → RS485 → Waveshare RS485 TO ETH → Ethernet → Your local network → Homey
The GTW-08 module exposes the heat pump’s Modbus registers via RS485. Since Homey communicates over your local network (TCP/IP), you need an RS485 to Ethernet converter to bridge the two protocols.
Configure the Waveshare converter with:
  • Protocol: Modbus TCP to RTU
  • Port: 502 (default Modbus TCP port)
  • Static IP address on your local network (so Homey can always reach it)
DEVICE PAIRING
Choose the Remeha Heat Pump device during pairing, select your heat pump model, and enter:
  • IP address of your GTW-08 / RS485-to-ETH converter
  • Port (default: 502)
  • Modbus slave ID (default: 100)
The app will test the connection before adding the device. You can optionally enable external energy meter capabilities during pairing or later in device settings.
STEP BY STEP INSTRUCTIONS
  1. Install the Remeha Modbus app from the Homey App Store.
  2. Set up the GTW-08 + RS485 to Ethernet converter on your local network (see HARDWARE SETUP).
  3. In Homey: Add new device → Remeha → Remeha Heat Pump.
  4. Select your heat pump model (Elga Ace Hybride Split, Monoblock or All-in-One Hybrid).
  5. Enter IP address, port and Modbus slave ID, then confirm.
  6. Watch the magic happen as the heat pump data is retrieved and displayed on the device card.
EXTERNAL ENERGY METER (OPTIONAL)
Want to see live power (W) and cumulative energy (kWh) from an external meter (P1, Shelly, HomeWizard, etc.) on your heat pump device?
Step 1 — In the device settings, enable:
  • Show power (W) from external meter — adds measure_power
  • Show energy (kWh) from external meter — adds meter_power
Step 2 — Create a single Flow:
When Your energy meter → Power has changed
Then Action 1: Set heat pump power (W) on your Remeha device → use the Power tag
Action 2: Set heat pump energy (kWh) on your Remeha device → use the Energy tag
After the Flow runs, your Remeha device shows live W + cumulative kWh and appears in Homey’s Energy dashboard (Grootverbruikers). Works with any energy meter in Homey — regardless of brand or protocol.
FLOW ACTION CARDS
Action Description
Set heat pump power (W) Push live power reading from an external meter
Set heat pump energy (kWh) Push cumulative energy reading from an external meter
Set electricity tariff peak Update peak electricity tariff (ct/kWh)
Set electricity tariff off-peak Update off-peak electricity tariff (ct/kWh)
Set gas tariff Update gas tariff (ct/m3)
VERSION HISTORY
  • 1.0.2 — [current LIVE release] Documentation updates, minor stability fixes.
  • 1.0.1 — Updated documentation with hardware setup instructions (GTW-08 + RS485 to Ethernet converter). Step-by-step guide for external energy meter Flow integration.
  • 1.0.0 — Initial release. Support for Elga Ace Hybride Split, Monoblock and All-in-One models. Real-time monitoring of 45+ registers via Modbus TCP. Thermostat, DHW, silent mode and hybrid mode control. Built-in Remeha energy counters. Optional external energy meter integration via Flow actions. Bilingual support (English and Dutch).
NOTES
  • This app uses the Modbus TCP protocol directly against the Remeha GTW-08 gateway — no cloud service involved.
  • Runs on both Homey Pro and Homey Pro Mini.
  • The register map is based on the official Remeha GTW-08 parameter documentation.
  • Developed and tested on Elga Ace Hybride Split. Let me know if other Elga variants work as well!
  • Modbus slave ID defaults to 100; adjust if your GTW-08 is configured differently.
  • You can update the GTW-08 connection settings (IP, port, slave ID) at any time via the device settings page — the app will automatically reconnect.
  • Remeha, Elga Ace and GTW-08 are trademarks of BDR Thermea Group.
KNOWN ISSUES
  • Some register readings may temporarily return 0 during heat pump start-up cycles.
  • COP reading is only meaningful when the heat pump is actively running.
  • When the RS485-to-ETH converter is power cycled, it may take up to 30 seconds before the app reconnects automatically.
TROUBLESHOOTING
If the device shows no data after pairing:
  1. Confirm the GTW-08 is correctly wired to the heat pump’s service connector.
  2. Confirm the RS485-to-ETH converter is set to Modbus TCP to RTU, port 502, and has a static IP on the same subnet as Homey.
  3. Verify the Modbus slave ID in the device settings matches the GTW-08 configuration (default: 100).
  4. Try power-cycling the RS485-to-ETH converter and wait ~30 seconds.
  5. If you use the Waveshare converter’s web UI, verify the RS485 baud rate matches the GTW-08 (typically 9600 8N1).
RELEASE version: Latest Version
Feedback, questions and model-compatibility reports are very welcome!
v1.1.0 is now available for testing.
Install (test): Remeha | Homey
Existing devices upgrade automatically — the new capabilities are
added on the next app start, no re-pairing needed.
Flow triggers
  • Defrost cycle started / ended
  • Error occurred (with error code and priority as tokens) / cleared
  • Status changed (with a dropdown to pick which status)
  • Hybrid mode changed
  • COP dropped below threshold (fires on the crossing, not continuously)
Flow conditions
  • Heat pump is actively heating
  • Heat pump is defrosting
  • Heat pump has an active error
  • Status is … (dropdown)
  • Hybrid mode is … (dropdown)
  • Domestic hot water is active
New status sensors decoded from the appliance status bitfields:
backup heater 1/2 active, DHW backup active, service required, water
pressure low, cooling active, solar thermal active.
COP switch threshold is now a writable capability (register HP054).
Use it to tune the crossover point when hybrid mode is set to
“Primary energy”.
What’s fixed
The hybrid-mode labels were wrong in v1.0.2. The label for value 0 was
“Boiler only”, which is the opposite of what the heat pump actually does.
Per the official Remeha documentation:
  • 0 = None (heat pump priority)
  • 1 = Cost-based
  • 2 = Primary energy (COP)
  • 3 = CO2-based
Value 3 was missing entirely. Existing flows keep working because the
IDs (0/1/2/3) are unchanged — only the displayed labels are different.
Tariff writes are now rate-limited to 6 per 24 hours as the Remeha spec
requires. Numeric writes are clamped to documented safe ranges (DHW
setpoint 35-65°C, room setpoint 5-30°C). Registers that aren’t
implemented on your model no longer show as -327.7°C or -1 kWh.
Known minor issues
Small things I want to fix in v1.1.1, not blocking the test:
  • meter_power.delivery_dhw may still show -1 on some models
  • meter_power.consumption_dhw may show an abnormally high value
  • Status shows “CV” during a DHW cycle instead of a dedicated DHW state
  • The COP threshold reads as empty until you write a value once
Feedback
Please try the beta and let me know in this topic:
  • Does the upgrade work on your existing device?
  • Do the new Flow cards behave as expected?
  • Any register issues on Elga variants other than the Hybride Split?
Is it possible to get this app to work on homey 2019?
v2.0.0 is now available for testing.
The app now runs on Homey’s Node.js runtime instead of Python. That is the
only reason it can be installed on Homey Pro (2016-2019).
Everything the app reads and writes is unchanged. After the port I diffed the
register map against the old one field by field: 57 registers, identical.
Before you update
This is the first release on the new runtime. Your device should carry over
with its settings and Flows, but I have not been able to test that upgrade
path myself. Please check your device after the update and post here if
anything is missing.
Runs on Homey Pro (2016-2019).
Optional network scan when you add a device. Leave the address field empty to
scan Homey’s own network. Type an address first to scan that subnet instead,
for example if the gateway sits in another VLAN.
All texts translated into the thirteen languages Homey supports.
What’s fixed
Status stayed on “Error” after a fault had cleared. It only reset on an app
restart and it hid every status change after it.
A heat pump that was unreachable at startup could stay marked unavailable
after it started answering again.
Thermostat mode offered “Cool”. The appliance has no cooling mode and it
silently switched to the schedule instead. New devices get Automatic, Heat
and Off.
Polling no longer starves itself. A full read cycle went from 57 Modbus
requests to 32 and takes about 2.5 seconds here. A register your model does
not have now drops out after three refusals instead of costing a timeout
every cycle.
Known minor issues
DHW comfort setpoint and COP threshold read as empty until you write a value
once. Those registers stay empty on the gateway until then.
The energy delivery meters carry thermal kWh but use the electrical meter
capability. Renaming them would break Insights history so that waits for a
bigger release.
Feedback
Please feel free to give any feedback
Hi, does it also work on the Remeha Confida MB400 series?
Hi Paul,
I connected with your app (test version) to the GTW-08 (connected to a Remeha Elga Ace 6kW split unit). It is connecting well, but not all data are populated.
I am aware that my GTW-08 is version 1.0.3, which does not support all registers (like the current 1.3 version).
Do you know if it is possible to update the firmware of the GTW-08?
v2.2.1 is now available for testing.
Existing devices upgrade automatically, no re-pairing needed. The new switch is added on the next app start.
CH function enabled: a switch for register 500. With it off, the heat pump ignores heating demand whatever the room setpoint, while hot water keeps working. It was off on my own unit and nothing in the app showed it.
Device setting “Log writes to the timeline”, off by default. Every value the app writes to the heat pump then appears in the timeline with the register and the value. A setting that changes without an entry was not changed through Homey.
Device icons per model: the indoor unit for the Hybrid Split, the control box for the Monoblock and the indoor unit with built-in boiler for the All-in-One.
Known minor issues
DHW comfort setpoint and COP threshold still read as empty until you write a value once.
Feedback
Does the CH function switch show up on your existing device?
With the log setting on, does a timeline entry appear when you change a value?
Which Elga model and GTW-08 version do you have, and which values stay empty?
Not tested, so I can’t promise it. I built the app on an Elga Ace Hybrid Split and Remeha’s GTW-08 Modbus v1.3 documentation. That documentation covers the Eria Tower Ace, the Elga Ace Monoblock, the All-in-One hybrid and the hybrid split. The Confida is not in it.
The MB 400 is sold with the ControlBox MB, which appears to be the same control box as the Elga Ace Monoblock (EHC-12 board), so it may work. As far as I can see Modbus is not built in.
If so I would happy to help.
I don’t know. I couldn’t find an update procedure for the GTW-08 from Remeha and none of the manuals I have mention firmware.
Can you tell me which values stay empty? Then I can compare them with the register list and see whether they are the ones your firmware lacks.
Thanks Paul.
The installer forgot to order the modbus adapter and waveshare rs485 ro ethernet converter. They’ll install it 14th if november. I will let you know.
I also believe it should work, being the same control box and all.
Cheers, Marc
Hello Paul, I saw that you built a nice Homey app to read the Remeha heat pump via Modbus. I am very interested in this now because, ever since the installation of the Elga Ace (hybrid 4kW), I have been bothered by the fact that you cannot communicate properly with the heat pump. I would like to know if you can also see the communication with the boiler in the app, such as heat demand, when the heat pump can no longer handle it on its own. Thanks in advance Regards, Arno