Not sure on what exact settings you need for the Eastrom SDM630, but the baud rate seems a bit high, I suggest starting with 9600 and see what happens.
Also, I see port 26 and 23 used, did you set those values? I would expect to see 502 there.
These are my settings for a similar waveshare device connected to a Growatt inverter:
(Suggestion: set the IP type to DHCP and add a reservation to your router if possible)
Thanks @DaneedeKruyff, not yet successful⊠changed baud rate, port (router is limited with these settings)also changed work mode:
Well, letâs take a closer look. What are the other options/combinations for Work mode?
Ok, TCP Server with Modbus TCP seems the right combintion to me, but what I only see just now in your screenshot, youâre using port 520 instead of 502.
Could you change that and try again?
good catch, but also not fixed it âŠFeel like a newbie here on this matter ![]()
Is there a way to see if the data is flowing, access in other mac tool or so?
Hi! Are there any ambitions to support Eastron SDM630 Modbus TCP?
From my understanding there is no need for a TCP gateway for this as it is already directly connected to the local network. I am still a novice in this area so I am eager to hear from you.
BR
Mathias
Hi Mathias, Yes, the âSDM630 Modbus TCPâ should be able to connect directly with Homey using the Eastron App, I havenât been able to test or check registers. I you have one test or sent the register list.
ï” Type: Ethernet
ï” Protocol: Modbus-TCP
ï” Modbus address range: 1-247
ï” IP: 192.168.1.200 (default)
ï” Port: 502
Hi Wout, this is what I found, hope it helps.
- Hardware Connection
-
Eastron SDM (RS485): Connect the A/T+ and B/T- terminals of the meter to the corresponding RS485 terminals on the converter.
-
Grounding: While RS485 can work without ground, it is recommended to connect the GND terminal of the meter to the converter for stability.
-
Ethernet: Connect the Converter to your network switch or router using a standard RJ45 cable.
-
Power: Power the converter (usually 6â36V) and ensure the Eastron meter is powered by the mains.
2. Converter Configuration (Web Interface)
Connect the converter to your network, find its IP address (default is often 192.168.11.121 or similar), and enter it into a web browser.
-
Work Mode: TCP Server.
-
Protocol: Modbus TCP to RTU (if available) or Transparent Transmission.
-
Baud Rate: 9600 bps (default for most Eastron meters).
-
Data Bits: 8.
-
Parity: None (or Even, depending on your meterâs setting).
-
Stop Bits: 1.
-
Local Port: 502 (standard for Modbus) or 8888.
3. Eastron Meter Setup
Ensure the meterâs internal settings match the converterâs serial parameters (Baud rate, parity).
- Modbus Address (Unit ID): Ensure each meter has a unique address if multiple are on the same bus (default is usually 1).
4. Troubleshooting
-
No Data: Check if A and B wires are swapped.
-
Parity Mismatch: Verify if your meter is set to âNoneâ or âEvenâ parity.
-
Address Conflict: If you have multiple meters, ensure they have unique addresses (e.g., 1, 2, 3).
-
Connection Timeout: Set the converter mode to
TCP Serverand ensure your firewall allows port 502
Thanks All, not yet successful, a bit further⊠Found my eastron settings and applied themâŠ
Set Baud 19.2
Set PArl NONE
Set StoP 2
SET rLY
SET rATE dFT
SET PULS 100
SET dlt 60
SET LP 60
SYS 3P4
SET Addr 005
Continue tonightâŠ
Great!
I have ordered but not yet received them.
Will try during April.
Br
Mathias