Hi, i probably need to change the “External EMS” parameter, because now i can’t control anything.
The problem is, that i have a case running @Growatt support, so i have to keep everyting the same for now.
From an HA post, i discovered the existance ShineWiLan-X2 for my MOD7000TL3-X inverter. So I purchased it last week and installed it yesterday, removing the white ShineLanBox from my meterkast :-). It also saves me a special Modbus connector and gateway.
Then, I discovered that you provided support form this. I have Homey Pro (2019). Nice.
Happy to test it !! (“have a Homey Pro with port forwarding enabled and configured in your router” - I have not set this up (yet).)
I want to limit the energy/export/output, in order to not export to the grid on my inverter (I have no battery - the TL3-X also does not support that).
I have set the ‘doelvermogen’. It can be set in steps of 5% of 7000, which seems fine.
The Homey app/device reflects this nicely.
The ShinePhone app seems to NOT reflect this. But that was a misconception from my part:
- the standard ‘Power’ graph gives the DC side.
- choosing ‘PAC’ (not sure what this. ‘Power AC’? ) nicely reflects the setting.
- (I think I need to create a CR for the ShinePhone) for this.
So for now, I am able to control 1 setting of the inverter. Nice!
I’ve also ordered a ShineWiLan-X2, which should arrive tomorrow. As soon as I have some spare time, I’ll install it, give it a test and share my findings.
Not shure why you’d need that, and it’s a major security risk.
These connection types don’t need port forwarding:
API: cloud connection
ModbusTCP: local connection
Plus, the port forwarding feature is only available for Pro 2023 and newer models.
That is so that I can do a remote cli app install from my development station. That is the only feasible way to analyse and debug a local (modbus) connection for me, since I do not have the hardware myself.
Clear! I didn’t find any instructions concerning port forwarding.
But it’s still not available for pre Pro 2023 models.
It is not needed for normal app users. Only one-time required for users that want to help me develop the modbus interface.
Yeah I tried to inform @johnv with that info, to save him from searching non-existent port forwarding settings on his
as he seems to try to enable port forwarding:
I did not enable this. It was not necessary.
v3.1.1 is ready for testing:
- Added export limit and grid charging for batteries in VPP mode
- Fixed min SoC on newer MIN TL-XH firmware
- Retry on Modbus timeouts
- Minor other fixes and improvements
Glad I could help! Thanks for taking the time to add new functions and fix things ![]()
I do not have a flow card ‘Set export limit’ for my device, using a Growatt MOD 7000TL3-X via ‘Inverter (modbus)’ with version 3.1.1 .
Changelog says: “3.1.0 : Added export limit, inverter status, heat alarm and fault codes to the Modbus inverter.” The app page does show this flow card.
Installing the app directly from the appstore might help
https://homey.app/en-nl/app/com.growatt/. Do not uninstall the existing app.
The export limit card only appears when the inverter has a Growatt meter. Your TL3-X has none, so use the power limit card instead.
New version 3.2.0 is published as stable:
- Fixed pairing of Modbus inverters that report their serial number elsewhere
- Added battery temperature for APX over Modbus
Ah, now I think of it, that makes sense. Without a connected meter, Growatt does not know how to curtail to 0.