Goedendag,  
Aangezien ik mijn opgewekte zonnestroom zoveel mogelijk zelf wil gebruiken, wil ik de boilertemperatuur van mijn mitsubishi warmtepomp gaan aanpassen. (via de app MELcloud).  
Dan wil ik de watertemperatuur verhogen zodra de zonnepanelen 7 kw exporteren.  
Voor met meten van de stroom gebruik ik de YOULESS P1 meter.

 ![Schermafbeelding 2025-02-02 122556](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/3/5/35691ccb1a626771985350973226e09cb62ad992.png)

Ik heb als test een flow gemaakt met onderstaande instellingen, maar helaas gebeurt er niets. (ik heb de instelde warmwatertemperatuur handmatig op 40 gr ingesteld.  
Als ik de test in de flow uitvoert dan wordt de ingestelde watertemperatuur wel aangepast.  
Wat gaat hier fout?

 ![Schermafbeelding 2025-02-02 123025](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/b/2/b228eb167b7a1b29025e9b2629ae7086e6343c90.png)

 ![20250202_120138000_iOS](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/f/f/ff66d2d8da56110ef3f664b6b42dfc7f748c6d6f.jpeg)

---

<div class="post-metadata">

**Author:** ![Theo\_de\_Koning](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/theo_de_koning/32/136062_2.png) [@Theo\_de\_Koning](https://community.homey.app/u/Theo_de_Koning)\
**Post date:** [February 2, 2025, 12:39pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/2 "2025-02-02T12:39:34Z")

</div>

Wanneer ik dit zo lees raak ik ook enigszins in de war.

-4405 is normaal kleiner dan - 3000.

In het licht van terugleveren weer niet.

Het wordt dan dus omdenken.

---

<div class="post-metadata">

**Author:** ![Rmb](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/rmb/32/79135_2.png) [@Rmb](https://community.homey.app/u/Rmb)\
**Post date:** [February 2, 2025, 12:49pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/3 "2025-02-02T12:49:40Z")

</div>

De flows triggeren niet, kan je checken door achter de WHEN kaart een melding in de tijdslijn toe te voegen . Je kijkt naar de verkeerde meter. Je moet het huidige vermogen kW hebben en niet de verbruikte energie kWh.

---

<div class="post-metadata">

**Author:** ![Peter\_Kawa](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/peter_kawa/32/173848_2.png) [@Peter\_Kawa](https://community.homey.app/u/Peter_Kawa)\
**Post date:** [February 2, 2025, 12:55pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/4 "2025-02-02T12:55:15Z")

</div>

Doe eens realistische waardes invullen, zoals 3 en -3 kW (1 kW = 1000 Watt) 😉

 ![1000042573](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/9/e/9ece46f82da73c08fab42177fd225c733bc524f4.jpeg)

En idd kWh is fout, huidig verbruik zou in kW moeten zijn, maar deze is hoogstwaarschijnlijk in W:

 ![1000042576](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/b/8/b8e85dd8ffba6526e6af2a6e445363842b6d4088.jpeg)

---

<div class="post-metadata">

**Author:** ![FKey](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/fkey/32/14793_2.png) [@FKey](https://community.homey.app/u/FKey)\
**Post date:** [February 2, 2025, 1:19pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/5 "2025-02-02T13:19:16Z")

</div>

> [@Johan\_Kluijfhout](#):
>
> Dan wil ik de watertemperatuur verhogen zodra de zonnepanelen 7 kw exporteren.

Beetje offtopic,  
maar hoeveel panelen heb je liggen?  
7kw teruglevering (export) is veel.  
Goede panelen doen 600 Wattpeak.  
Dus op een ideale dag met ideale ligging en geen verbruik moet je 12 panelen hebben om 7kwh te produceren.

En je warmtepomp staat al aan.

Op de P1 meet je het overschot, dus het verbruik van de warmtepomp is al van de opbrengst af.

Dus of die flow ooit gaat lopen met 7kw? (Hangt vooral af van het aantal panelen die je hebt liggen)

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 2:48pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/6 "2025-02-02T14:48:18Z")

</div>

Ik heb 42 panelen liggen

Groeten, Johan

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 4:39pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/7 "2025-02-02T16:39:58Z")

</div>

Zou dit dan wel goed moeten zijn?

 ![Schermafbeelding 2025-02-02 173441](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/1/2/125c476c9ee5f228c3bfaa2dc22b5c991dd82ade.png)

In de MELcloud app blijft de warmwatertemperatuur instelling op 49 graden staan.

 ![20250202_163609000_iOS](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/4/b/4b18f7de63d46063f11a5eba358802145ce00352.jpeg)

---

<div class="post-metadata">

**Author:** ![FKey](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/fkey/32/14793_2.png) [@FKey](https://community.homey.app/u/FKey)\
**Post date:** [February 2, 2025, 4:50pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/8 "2025-02-02T16:50:04Z")

</div>

> [@Johan\_Kluijfhout](#):
>
> Ik heb 42 panelen liggen

Mini power plant 😀

---

<div class="post-metadata">

**Author:** ![FKey](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/fkey/32/14793_2.png) [@FKey](https://community.homey.app/u/FKey)\
**Post date:** [February 2, 2025, 4:57pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/9 "2025-02-02T16:57:07Z")

</div>

> [@Johan\_Kluijfhout](#):
>
> Zou dit dan wel goed moeten zijn?

Dat zie er goed uit.  
Voeg een [simple log](https://homey.app/en-nl/app/nl.nielsdeklerk.log/Simple-(Sys)-Log/) kaartje toe aan de flow.  
Dan kan je zien of de flow triggert

---

<div class="post-metadata">

**Author:** ![JohanP](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johanp/32/119002_2.png) [@JohanP](https://community.homey.app/u/JohanP)\
**Post date:** [February 2, 2025, 5:36pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/10 "2025-02-02T17:36:40Z")

</div>

-4405 is AL kleiner dan -7000, dus triggert niet ?  
Ik zou iets doen als : ALS export veranderd EN export is groter dan -7000 DAN temp op 60C

Nb 45C is wel (gevaarlijk ?) laag ivm legionella? Tenzij je regelmatig legionellaruns doet…

---

<div class="post-metadata">

**Author:** ![Peter\_Kawa](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/peter_kawa/32/173848_2.png) [@Peter\_Kawa](https://community.homey.app/u/Peter_Kawa)\
**Post date:** [February 2, 2025, 5:56pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/11 "2025-02-02T17:56:41Z")

</div>

Precies! Loggen loggen loggen 😬  
Voorbeeldje voor @Johan_Kluijfhout

 ![Screenshot from 2025-01-27 13-12-23](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/f/7/f7025c540e43c2c8278ea97e3e9519b81b887f55.png)

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 6:07pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/12 "2025-02-02T18:07:12Z")

</div>

Ga ik proberen, thanks  
Mitsubishi heeft een wekelijkse legionella programma.

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 6:11pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/13 "2025-02-02T18:11:08Z")

</div>

Ik heb ALS export verandert toegevoegd, maar dan heb ik bij vervolgstap EN alleen deze mogelijkheid:

 ![Schermafbeelding 2025-02-02 190909](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/d/a/da467035f3f4b4aa14e0f327b3975b8e24249eb3.png)

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 6:21pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/14 "2025-02-02T18:21:54Z")

</div>

Beste Peter,  
Dank voor je reactie.  
Ik ben nog niet zo lang in het bezit van een homey.  
Ik heb wel al een aantal flows gemaakt maar deze zijn nog redelijk simpel.  
Deze LOG app ken in nog niet.  
Waar voeg je die dan toe als ik bij ALS het vermogen onder de -7000 watt komt DAN de watertemperatuur op 60 graden zetten?

---

<div class="post-metadata">

**Author:** ![Wim\_Post](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/wim_post/32/56793_2.png) [@Wim\_Post](https://community.homey.app/u/Wim_Post)\
**Post date:** [February 2, 2025, 6:26pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/15 "2025-02-02T18:26:59Z")

</div>

![Schermafbeelding 2025-02-02 173441](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/1/2/125c476c9ee5f228c3bfaa2dc22b5c991dd82ade.png)

Stel de warmtepomp verbruikt 1000 watt en de teruglevering wordt 7500 watt. Dat is meer dan 7000 watt, dus de warmtepomp slaat aan. Daardoor daalt de teruglevering naar 6500 watt en dus slaat de warmtepomp uit. Dan stijgt de teruglevering weer naar 7500 watt. Dus slaat de warmtepomp weer aan. Enz. Enz.

---

<div class="post-metadata">

**Author:** ![Peter\_Kawa](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/peter_kawa/32/173848_2.png) [@Peter\_Kawa](https://community.homey.app/u/Peter_Kawa)\
**Post date:** [February 2, 2025, 6:47pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/16 "2025-02-02T18:47:08Z")

</div>

Graag gedaan.  
Het kan ook met tijdlijn kaartjes bijv., maar die is onbetrouwbaar (kan rate limits krijgen zonder enige notificatie).

> [@Johan\_Kluijfhout](#):
>
> Waar voeg je die dan toe als ik bij ALS het vermogen onder de -7000

Knoop een notificatie kaartje achter de trigger; zo weet je óf, en wanneer de flow werd getriggerd;  
Optioneel: Ik voeg dan ook de actuele waarde waarop getriggerd moet worden toe aan de notificatie:

 ![1000000413](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/a/6/a61d43e9204e16282e651058076d4de67bda216e.jpeg)

Zo zou het kunnen worden:  
Hier heb ik het meeste wel gelogd en vastgelegd, incl. eventuele errors van de actiekaart:

 ![1000000417](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/d/e/de7f8274edddce34b81ff852b0ae1cec39a7de47.jpeg)

---

<div class="post-metadata">

**Author:** ![FKey](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/fkey/32/14793_2.png) [@FKey](https://community.homey.app/u/FKey)\
**Post date:** [February 2, 2025, 7:39pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/17 "2025-02-02T19:39:35Z")

</div>

> [@JohanP](#):
>
> -4405 is AL kleiner dan -7000, dus triggert niet ?

Uuuh -4405 is groter dan -7000….  
We hebben het over negatieve getallen.

---

<div class="post-metadata">

**Author:** ![FKey](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/fkey/32/14793_2.png) [@FKey](https://community.homey.app/u/FKey)\
**Post date:** [February 2, 2025, 7:46pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/18 "2025-02-02T19:46:01Z")

</div>

> [@Wim\_Post](#):
>
> Stel de warmtepomp verbruikt 1000 watt en de teruglevering wordt 7500 watt. Dat is meer dan 7000 watt, dus de warmtepomp slaat aan. Daardoor daalt de teruglevering naar 6500 watt en dus slaat de warmtepomp uit. Dan stijgt de teruglevering weer naar 7500 watt

Je moet de stroom van de warmtepomp dus meenemen in de berekening.

Heeft de warmtepomp een stroomuitlezing naar homey? Dan is het makkelijk.  
Anders kan je initieel nog met een afschartting werken.

Kijk eens naar [mijn flow](https://community.homey.app/t/app-amina-power-up-your-smart-home-with-amina-s/114193/6) voor aansturing. Van mijn laadpaal.  
Daar regel ik naar nul op de meter.  
In die berekening gebruik ik ook

---

<div class="post-metadata">

**Author:** ![G-J-T](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/g-j-t/32/86581_2.png) [@G-J-T](https://community.homey.app/u/G-J-T)\
**Post date:** [February 2, 2025, 8:38pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/19 "2025-02-02T20:38:45Z")

</div>

De verandering van de temperatuur triggert niet meteen een SWW-run. Je moet eigenlijk na het instellen van de temperatuur er een opdracht achteraan laten komen die een geforceerde SWW-run (gedwongen) uitvoert. Dan gaat ie vervolgens wel aan de slag.

 ![IMG_2443](https://us1.discourse-cdn.com/flex025/uploads/athom/original/3X/b/4/b44f8c73ed5eb8755bda41fa8c3eaf7fd42d5356.jpeg)

---

<div class="post-metadata">

**Author:** ![Johan\_Kluijfhout](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/johan_kluijfhout/32/78869_2.png) [@Johan\_Kluijfhout](https://community.homey.app/u/Johan_Kluijfhout)\
**Post date:** [February 2, 2025, 9:25pm UTC](https://community.homey.app/t/watertemperatuur-boiler-mitsubishi-warmtepomp-instellen/129544/20 "2025-02-02T21:25:20Z")

</div>

Als de zonnestroom terugloopt en de watertemperatuur weer terug gaat naar 40 graden, moet ik de SWW dan weer op automatisch zetten of kan dit altijd op gedwongen blijven staan?