# Board unreachable from Homey (timeout) while Modbus TCP port 502 is confirmed open from a PC on the same subnet

**URL:** <https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681>\
**Category:** Questions & Help\
**Created:** [September 16, 2026, 7:45pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681 "2026-09-16T19:45:04Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Twan\_Van\_Hal](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/twan_van_hal/32/16677_2.png) [@Twan\_Van\_Hal](https://community.homey.app/u/Twan_Van_Hal)\
**Post date:** [September 16, 2026, 7:45pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681/1 "2026-09-16T19:45:04Z")

</div>

Hi, I’m running into a persistent “Timed out waiting for Waveshare response” and hope you can help pinpoint it.

Setup:

- Homey Pro 2026, wired Ethernet, IP 192.168.1.241
- Waveshare Modbus POE ETH Relay (8-channel), firmware V1.486, fixed IP 192.168.1.91, port 502, Modbus device ID 1, Work Mode TCP Server, “Modbus TCP to RTU” enabled, Multi-TCP Connection enabled
- Network: UniFi (UDM SE + US-24 switch), no VLAN separation; Homey reaches all my other local LAN devices without issue

What I have verified:

- From a Windows PC on the same subnet (192.168.1.232): Test-NetConnection 192.168.1.91 -Port 502 returns TcpTestSucceeded: True. Confirmed twice, with VirCom fully closed (also killed via Task Manager).
- Ping to 192.168.1.91 succeeds, 0% packet loss
- Board power-cycled several times (PoE unplugged 30s)
- App fully uninstalled and reinstalled; board re-added through Add Device → Waveshare Relay
- Tried polling interval 100 ms and 1000 ms, response timeout 750 ms and 2000 ms

Result: the PC connects to port 502 without any problem, but the Homey app keeps timing out. Live status shows “Last successful poll: never” with consecutive errors climbing. Board settings in the app are 192.168.1.91:502, Modbus ID 1.

Question: could there be something in how the app opens or frames the Modbus TCP session that this Waveshare model does not answer, even though a plain TCP connection to port 502 succeeds from another client on the same subnet? Happy to run any diagnostics or share a diagnostic report.

---

<div class="post-metadata">

**Author:** ![Peter\_Kawa](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/peter_kawa/32/173848_2.png) [@Peter\_Kawa](https://community.homey.app/u/Peter_Kawa)\
**Post date:** [September 16, 2026, 8:16pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681/2 "2026-09-16T20:16:35Z")

</div>

> [@Twan\_Van\_Hal](#):
>
> Modbus ID 1

Tried other IDs, like ID 0?

---

<div class="post-metadata">

**Author:** ![Twan\_Van\_Hal](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/twan_van_hal/32/16677_2.png) [@Twan\_Van\_Hal](https://community.homey.app/u/Twan_Van_Hal)\
**Post date:** [September 16, 2026, 8:28pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681/3 "2026-09-16T20:28:01Z")

</div>

Changed it to ID:0 but stil a timed out error

---

<div class="post-metadata">

**Author:** ![smarthomesven](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/smarthomesven/32/79712_2.png) [@smarthomesven](https://community.homey.app/u/smarthomesven)\
**Post date:** [September 16, 2026, 8:37pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681/4 "2026-09-16T20:37:09Z")

</div>

The readme mentions that you have to add it using the Configure page first:

> [@](#):
>
> Click Test new board and confirm the board responds. Then click Save for Add Device. After that, use Homey’s normal Add Device flow to add the Waveshare relay devices and/or Waveshare contact input devices.

Have you done this?

---

<div class="post-metadata">

**Author:** ![Twan\_Van\_Hal](https://sea1.discourse-cdn.com/flex025/user_avatar/community.homey.app/twan_van_hal/32/16677_2.png) [@Twan\_Van\_Hal](https://community.homey.app/u/Twan_Van_Hal)\
**Post date:** [September 16, 2026, 10:05pm UTC](https://community.homey.app/t/board-unreachable-from-homey-timeout-while-modbus-tcp-port-502-is-confirmed-open-from-a-pc-on-the-same-subnet/159681/5 "2026-09-16T22:05:52Z")

</div>

**1. Transfer Protocol was None** (VirCom → Device Settings). The board then forwards Modbus TCP unchanged to the internal RS485 bus, where the relay chip does not recognise the MBAP header and never replies. Set to **Modbus TCP protocol** → Modify Setting → Restart Dev. Close VirCom fully afterwards.

```
**2.	Modbus ID is 1** , not 0.

**3.	The board only supports coil functions.** FC01 replies; FC02/03/04 return nothing. The Waveshare app also polls the contact inputs, times out there and fails the whole cycle — which is why "Test this board" passed while the board stayed offline. No setting to disable it.

```

**Fix:** generic Modbus app (org.modbus), device type **Modbus Device**. Port 502, unit ID 1. Write Coil on addresses 0–7 for CH1–CH8, Read Coil to read back. Only sends what you put in a flow card, so FC02 is never requested.

Tip: an open port 502 proves the TCP handshake, not that the board answers Modbus. Test the function codes individually from a PC.